Hey GregBrew, is this pretty much the kit you designed and built yourself?

Further information on my setup.

I tied the negative cable of my inverter under-hood connector to the same location that the vehicle battery negative terminal is attached to. The vehicle battery negative cable goes through a toroidal current sensor, then to the grounding stud. The inverter under-hood connector negative cable does not go through the current sensor. The grounding stud is on the drivers side wheel well, and as such is a PITA to get to, but I struggled and was successful. I highly recommend being very careful about dropping anything (like tools) when you're elbow deep under the hood. I didn't drop anything, but I'm uncertain if it would be retrievable if I did. There are also several sharp metal surfaces in there. I have multiple superficial cuts on my hands to prove it.

I modified the procedure a bit. I've chosen to shift the Bolt into "L" before exiting from the passenger side, instead of "N". I'm doing this because the Bolt will hold its position when in "L", and it won't while in "N". I don't know if there's any power use difference between the two. (If any of you know, please speak up.) Of course, the Bolt has the parking brake set in either case.

I hooked up a 1500W pure sine-wave inverter, and plugged in a (heat shrink type) heat gun as a load. The heat gun has two settings: 900W and 1200W. Note that these are both on the load side of the inverter, so the vehicle draw is probably closer to approximately 1100W and 1500W, considering conversion efficiencies. Unfortunately, I don't own a DC clamp-on current meter.

Load current was provided by a Watt's Up meter.
At 1200W AC load, the vehicle DC-DC couldn't keep up, and the aux battery voltage dropped slowly.
At 900W AC load, the battery voltage cycled between 13.66V and 13.88V, measured with a reliable multimeter. I suspect that these values represent the hysteresis of the DC-DC to AGM battery system..."on" when the battery drops below 13.66, and "off" when it gets to 13.88. The cycling rate was probably every 5-10 seconds. That's a lot of cycles, but the cycle rate with a realistic load should be much slower.

I'm going to let it run with the 900W AC load for a couple of hours to verify that the system functions as expected. Using a gun-type IR temperature meter, I checked connection temperatures at the studs where the inverter cable is connected to the battery and grounding stud, as well as everywhere else, and am seeing no temperature rise beyond ambient. Surprising, when you consider I'm drawing around 100A through them all.

FYI. When I tried tying the ground lead elsewhere than the designated stud, I first-degree burned my fingers testing for temperature rise. Stupid!
 

·
Registered
Joined
·
4,841 Posts
Not to detract from any of the inverter setups folks have set up to run off their 12 volt battery...it still drives me nuts that every new EV has a 7+ kW onboard inverter that could be made to send power back out for a few dollars worth of redesign. I ask again...Why will none of the manufacturers put these outlets in the storage compartment of their EVs?


Places like Lowes sells thousands of these every year, to any yahoo that can fog a mirror, yet EV owners can't be trusted to use this responsibly?

 

·
Registered
Joined
·
2,611 Posts
Hey GregBrew, is this pretty much the kit you designed and built yourself?

Pretty much. The Bolt kit wasn't available when I made my own. Mine was somewhat based on their kit for the Volt, that I had purchased and installed.
 

·
Registered
Joined
·
2 Posts
I have built my own system per the parts list by GregBrew (ThankYou!) in this excellent thread for my '19 Bolt and it is working great on all resistive loads I've tested it on up to about 1000 watts max. Everything that is, except my fridge– arguably my highest priority item. I must have the least energy efficient fridge on the planet. It doesn't run all the time, and when it does it's usually reading about 1 amp, occasionally I see short spells of 6.25 amps. But starting up after I first plug it in can see the ammeter spike up to 18.5 amps for less than a second before it settles down. I assume this is the Locked Rotor Amps (LRA) of the fridge's compressor motor?
Anyway, with no other loads running in the house, as soon as I plug the fridge in, it is enough to put both of the inverters I've tried into alarm mode an shut down the output. I have tried two different inverters, a 1500 watt and then, thinking I might need something a little more robust, a 3000 watt- both pure sine wave.
The fridge is a GE Model #: GTH17JBXWW Energy Star 16.5 Cu Ft Top-Freezer Refrigerator. Technical Data sheet attached.
I'm curious before we run out and buy a new fridge if this is really the problem. How does this compare to what others are using? Could it be fate that the 2 inverters I picked were both poor quality, or...?
 

Attachments

·
Registered
Joined
·
42 Posts
those trashy inverters will never yield that power that they advertise. I think the inverter rating of 1500 or 3000 watts is a measure the power consumption of the inverter when running at full power and not the power it can provide. I have a Xantrex PROwatt 2000 watt inverter. Got it because the max out of the Bolt is 16 amps at 12v. Installed a 150 amp fuse between the Bolt and the inverter (when in use) to make sure I don't hurt my baby bolt. I can run my refrigerator on it but nothing else. Of course, I can run a lot of stuff as long as the refrigerator is not plugged in. I needed it only for emergencies and that solves my problem. My guess is you inverter is not cutting it. Good luck!
 

·
Registered
Joined
·
393 Posts

·
Registered
Joined
·
2 Posts
^^^
My Samlex 1000W 12VDC to 120VAC Pure Sine Inverter | PST-1000-12 (PST-1000-12) can run my fridge, some lights (CFL and LED), charge my laptop, phone, and my 7 camera NVR system all together just fine.

As the manual at https://www.samlexamerica.com/documents/manuals/11001-PST-1000-12-24_0220_Hrez.pdf points out (like on pages 10 and 14), there's the issue of surge power needed to startup some appliances like fridges and about you can do is guess.
I just got a Samlex 1500W for my Bolt and the difference between it and the other 2 cheap inverters I tried is like night and day. The Samlex is a quality unit in every way, including documentation that is so complete and well-written it is like a text book for this type of equipment. I tried a pure sine wave LVYUAN 1500W and a WZRELB 3000W inverter and neither one could handle the loads that the Samlex can. You also need a multi-meter that can record max inrush AC current to properly size your inverter if you are planning on powering induction-type loads (like a refrigerator).
 